Minimum Power of Water Cooler for Thermal Load Device
A water cooling unit with a storage volume of cools water at a constant rate of . In a closed circulation setup (as depicted in the figure), water from this cooler cools an external device that generates a constant thermal load of . The temperature of the water entering the device must not exceed , and the initial temperature of all of stored water is . Assuming the system is thermally insulated, find the minimum cooling power (in watts) required to operate the device for .
(Specific heat capacity of water is and density is )

Options
1600
2067
2533
3933
Topics & Concepts
Step-by-Step Solution
To find the minimum cooling power required to operate the external device for , we perform a total thermal energy balance on the closed system.
1. Identify Given Parameters
- Storage volume of water,
- Density of water,
- Specific heat capacity of water,
- Initial temperature of water,
- Maximum allowable temperature of water,
- Thermal load of the device,
- Operation time,
2. Energy Balance Calculation
The total heat energy added to the water in time increases its temperature from to the maximum permitted value of .
The maximum allowable heat energy accumulated in the water is:
Substituting the values:
The net rate of heat input into the water system is the difference between the heat generated by the device and the heat removed by the cooler:
The total net heat transferred to the water in time is:
3. Solving for Minimum Power
Equating the two expressions for :
Rounding off to the nearest integer gives:
Conclusion
The minimum cooling power required is .
Correct Option: (B)